Authorized Setting of the Blocking Lock

The ‘Authorised Setting‘ functionality extends the setting and unsetting procedure for a Blocking Lock with a second security level. Before the system can be set or unset, a code must be entered on an external setting device such as a card or pin reader with a separate controller. This controller can be connected to any kind of intrusion system using inputs and outputs.

Operation is as follows:

  1. The panel signals to the external setting device when it is possible to set using a Ready To Set output.

  2. When the code is entered, the Setting Authorisation input is activated and Blockschloss 1/2 is activated.

  3. The blocking lock opens a control panel input (Keyarm) which initiates the setting procedure of the panel.

  4. The external setting device waits up to 8 seconds for Fullset Done output signal to be activated from the control panel.

  5. If this signal is not received, the setting fails and the external setting device unsets the system again.

The configuration requirements for Authorised Setting are as follows:

  • Area Attributes:

    – Setting Authorisation

    Set

    Set and Unset (required for VdS)

    Unset

  • Outputs:

    – Ready to set

    – Setting Ack

    – Fullset Done

  • Inputs

    – Keyarm