Authorized Setting of the Blocking Lock
The ‘Authorised Setting‘ functionality extends the setting and unsetting procedure for a Blocking Lock with a second security level. Before the system can be set or unset, a code must be entered on an external setting device such as a card or pin reader with a separate controller. This controller can be connected to any kind of intrusion system using inputs and outputs.
Operation is as follows:
-
The panel signals to the external setting device when it is possible to set using a Ready To Set output.
-
When the code is entered, the Setting Authorisation input is activated and Blockschloss 1/2 is activated.
-
The blocking lock opens a control panel input (Keyarm) which initiates the setting procedure of the panel.
-
The external setting device waits up to 8 seconds for Fullset Done output signal to be activated from the control panel.
-
If this signal is not received, the setting fails and the external setting device unsets the system again.
The configuration requirements for Authorised Setting are as follows:
-
Area Attributes:
– Setting Authorisation
Set
Set and Unset (required for VdS)
Unset
-
Outputs:
– Ready to set
– Setting Ack
– Fullset Done
-
Inputs
– Keyarm